No Main Breaker
daveselectric
Ohio
As I recall under the six switch rule, the breakers may not be any smaller than 30 amps. Any comments? What is the code reference?
Thanks,
Re: No Main Breaker
230.90 (A) Ex 2 Fuses and circuit breakers with a rating or setting that conform with 240.4(B) or (C) and 240.6 shall be permited.
[ March 03, 2005, 05:22 PM: Message edited by: tshea ]
Re: No Main Breaker
I believe you are thinking of the requirement that panels supplying circuits (with a neutral) smaller than 30A are considered lighting and branch circuit panels and therefore require a main breaker.
Re: No Main Breaker
215.2 Minimum Rating and Size.
(A) Feeders Not More Than 600 Volts.
2) For Specified Circuits. The ampacity of feeder conductors shall not be less than 30 amperes where the load supplied consists of any of the following number and types of circuits: NEC 2002
This is deleted in the 2005
Charlie
[ March 04, 2005, 01:33 PM: Message edited by: cpal ]
Re: No Main Breaker
I beleive the correct code reference would be to apply 225.39((A), (B), (C) or (D) depending upon your application.