It appears they finally outlawed shared neutrals for emergency circuits in the 2014 NEC. 700.19 states
It also appears they are slowly trying to require some type of emergency lighting in panels rooms, at least for the main disconnecting means. They added to 700.16
What do you think of this?
2014 NEC said:... "The branch circuits serving emergency lighting and power circuits shall not be part of a multiwire branch circuit.
It also appears they are slowly trying to require some type of emergency lighting in panels rooms, at least for the main disconnecting means. They added to 700.16
2014 NEC said:... Where an emergency system is installed, emergency illumination shall be provided in the area of the disconnecting means required by 225.31 and 230.70 as applicable, where the disconnecting means are installed indoors.