hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have generator which plans show is separately derived, wye windings, however ATS is 3 poles, and there are no neutral loads or unbalanced loads so no neutral is brought from gen to load. The gen has main breaker.
Questions:
1. I thought in order to be separately derived ATS has to be 4 poles no?
2. Gen Wye winding would have to be grounded with GEC and GES regardless of neutral or no neutral at the GEN no?
3. How would this work no neutral? Should their be system bonding jumper at gen main breaker above situation?
4. Where would the EGC connect to if no system bonding jumper at the GEN?
5. In the event load becomes unbalanced in future would not be objectionable current thru EGC thru metallic enclosure thru system bonding jumper to GEN i.e EGC act as neutral?
Sent from my iPhone using Tapatalk
Questions:
1. I thought in order to be separately derived ATS has to be 4 poles no?
2. Gen Wye winding would have to be grounded with GEC and GES regardless of neutral or no neutral at the GEN no?
3. How would this work no neutral? Should their be system bonding jumper at gen main breaker above situation?
4. Where would the EGC connect to if no system bonding jumper at the GEN?
5. In the event load becomes unbalanced in future would not be objectionable current thru EGC thru metallic enclosure thru system bonding jumper to GEN i.e EGC act as neutral?