Twoskinsoneman
Senior Member
- Location
- West Virginia, USA NEC: 2020
- Occupation
- Facility Senior Electrician
We had a vfd installed for a pump. I did not do it. I got called because the vfd won't start due to high system voltage. The voltage on the 480v system has always been high. At 505v this is the first time I've seen a vfd that wouldn't accept it. Rather than deal with the system voltage admin wants to just fix this particular problem. Is a buck boost transformer the best option for getting this wrapped up? It's a small 8.5FLA pump. 7.06kva buck transformer for this touchy vfd?