Can anyone guide me to the appropriate article in the NEC 2008 on how to calculate the ampacity for the conductors feeding a single phase 240 volt non-continuous loads due to a resistance heater?
Aren't all fixed electric space heating equipment considered continuos loads regardless of anything else so long its the branch circuit 125%?? NEC 2008 424.3(B) Feeders are 220.51 at a 100%, not 125%
Sure, but there can be resistance heaters that are not space heating equipment. Like a pvc hot box, or an iron, or a cooktop.
240 volt non-continuous loads . . . Either current from the nameplate, or ohms law for amperage. Section 310.15 will help you choose the right conductor.