Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
Good Evening fellow Sparky's
First -
NEC 220.40 and 230.79 Both basically say use Part II of 220 to calculate the service size. Article 220 Part II does not include anything about only the larger of the 2 loads heating or air conditioning for a non-dwelling unit being included as part of the service loads.
220.18 (A), makes no sense to me, can someone explain?
Second -
Part II of article 220 says nothing about needing to use 125% of continuous loads when calculating service loads it states each of the different loads to be used when performing the service calculations.
I see 220.14(C) tells you to use 430.22 for motor outlets which in turn says to use 125% of the motor load.
Obviously the 125% is part of branch circuits article 210.20.
Third -
Why is 220.18 (B) even in there. If I calculated my load for lighting based on 220.12 what is the point in mentioning this about LED lighting?
Thanks for looking.
First -
NEC 220.40 and 230.79 Both basically say use Part II of 220 to calculate the service size. Article 220 Part II does not include anything about only the larger of the 2 loads heating or air conditioning for a non-dwelling unit being included as part of the service loads.
220.18 (A), makes no sense to me, can someone explain?
Second -
Part II of article 220 says nothing about needing to use 125% of continuous loads when calculating service loads it states each of the different loads to be used when performing the service calculations.
I see 220.14(C) tells you to use 430.22 for motor outlets which in turn says to use 125% of the motor load.
Obviously the 125% is part of branch circuits article 210.20.
Third -
Why is 220.18 (B) even in there. If I calculated my load for lighting based on 220.12 what is the point in mentioning this about LED lighting?
Thanks for looking.