Non dwelling units countertop requirements
shortcircuit1
USA
If you have a business center which has a counter top space including dishwasher and disposal.It also has a refrigerator.I was debating whether there are any requirements for counter top spaces in non dwelling units.Do i still have to follow 2 SABC rule for this?
If you had permanent provisions for cooking then I would say you had a kitchen and would need all the receptacles to be on gfci
I dont think having a dishwasher and disposal can be considered as permanent provisions for cooking.In that case i dont need to provide two SABC's.Two dedicated ckts for dishwasher and disposal should do the job.
I didn't say that... I said IF you had....
BTW, two small appliance branch circuit's is only required for residences
I agree that the two SABCs are not needed. I don't know New York rules. But the ability to wash utensils is enough for WA to call it a kitchen. That would require GFCI for any receptacle in the area. How you put a boundary on that "area" is a bit trickier.
I think I'd be inclined to just add a couple 20 A circuits as they will probably be needed.
I think I would also make them GFCI.
They can afford the few extra bucks.
What if someone wants to put a countertop microwave or a toaster?
Well most likely they would not be hardwired so they wouldn't be considered "permanent" and on another note, "what ifs" are not a concern, you can not control what happens after you're gone.
Roger
Roger
I agree but if you move in to a space and you have this counter top space with no receptacles then people tend to start using extension cords from the nearest outlets.I would put at least one cause now a days everyone has a coffeemaker or microwave.
I might would ask them where the Microwave is going to be, It may be an extra charge, of course.
Stay to the prints if you have one.
Worked with a guy who gave openings away, "we will get more business when they see what a great job we do!".
Never got "more", I think they just laughed at what a bunch of goofs we were giving free stuff.