dan filipi
Member
We've been doing alot of swimming pool upgrades lately, most times the #8 bond conductor isnt connected to ANY of the equipment. Scarey, but at least it exists to be corrected.
Anyway,this current job is upgrading all electrical to current code at the pool. The pool was built early 60's, no light GFCI, aluminum Bell box as deck box.
The #8 bond is nowhere to be found, maybe buried in concrete, who knows, and it may be that it was never installed to the equipment from the bonding grid back in the 60's.
I need to tie into the bonding grid in some way.
In looking through article 680.26 Bonding.
680.26 (C) states "The common bonding grid shall be permitted to be any of the following: (# 4 states) "Rigid metal conduit or intermediate metal conduit of brass or other identified
corrosion -resistant metal conduit".
The way I'm understanding this is, If I clamp to the light niche brass riser conduit, this is a recognised and acceptable point to tie into the bonding grid. Is this an accurate understanding?
My concern here is that if the pool steel, light niche etc. were not properly bonded together when the pool was built, by my tieing into the brass pipe to bond the motor, is there any chance am I actually CREATING a difference in ground potential if structural bonding was not done? I dont think so but want to be certain.
All of the equipment conduits are being rewired so all EGC connections will be verified done properly at that point.
Any input much appreciated,
Dan
[ January 26, 2005, 06:59 PM: Message edited by: danl ]
Anyway,this current job is upgrading all electrical to current code at the pool. The pool was built early 60's, no light GFCI, aluminum Bell box as deck box.
The #8 bond is nowhere to be found, maybe buried in concrete, who knows, and it may be that it was never installed to the equipment from the bonding grid back in the 60's.
I need to tie into the bonding grid in some way.
In looking through article 680.26 Bonding.
680.26 (C) states "The common bonding grid shall be permitted to be any of the following: (# 4 states) "Rigid metal conduit or intermediate metal conduit of brass or other identified
corrosion -resistant metal conduit".
The way I'm understanding this is, If I clamp to the light niche brass riser conduit, this is a recognised and acceptable point to tie into the bonding grid. Is this an accurate understanding?
My concern here is that if the pool steel, light niche etc. were not properly bonded together when the pool was built, by my tieing into the brass pipe to bond the motor, is there any chance am I actually CREATING a difference in ground potential if structural bonding was not done? I dont think so but want to be certain.
All of the equipment conduits are being rewired so all EGC connections will be verified done properly at that point.
Any input much appreciated,
Dan