They would not be taps.For an ag service, is it permissable to install a non-fused service entrance switch under the meter, then run undergound conductors to multiple pump panels, each with its own OCPD? Sort of combining the 6 handle and unlimited length outside feeder tap rules . . .
I don't see how you can get around 230.91For an ag service, is it permissable to install a non-fused service entrance switch under the meter, then run undergound conductors to multiple pump panels, each with its own OCPD? Sort of combining the 6 handle and unlimited length outside feeder tap rules . . .
I think it's because Art 547 identifies the pole disconnect as a site isolation device with each individual building having it's own service disconnectI don't see how you can get around 230.91
Some of the POCOs in this area used to provide disconnects under their meters. They were never considered the SE for the farm. Each building or grain bin would have its own. Pump Panels can be SUSE.I don't see how you can get around 230.91
Ok yeah, read it a little more thoroughly and I see it now, neat. Should this be referenced in 230.82?I think it's because Art 547 identifies the pole disconnect as a site isolation device with each individual building having it's own service disconnect
So to answer the op, I would say yes that is acceptable but not for the reasons you state. It seems the service disconnect and ocpd still need to be adjacent, but you can choose to either Mount them at the distribution point or at each building. If you have a disconnect only at the distribution point, you can consider it the site isolation device, feeding service conductors, and the service disconnect is at each building (with the OCPD).For an ag service, is it permissable to install a non-fused service entrance switch under the meter, then run undergound conductors to multiple pump panels, each with its own OCPD? Sort of combining the 6 handle and unlimited length outside feeder tap rules . . .
All the rural POCO's here provide that disconnect at the pole, often is a meter and disconnect combination, some have OCPD's some don't, as mentioned some even have a manual transfer switch incorporated into them - usually with no OCPD's though.So to answer the op, I would say yes that is acceptable but not for the reasons you state. It seems the service disconnect and ocpd still need to be adjacent, but you can choose to either Mount them at the distribution point or at each building. If you have a disconnect only at the distribution point, you can consider it the site isolation device, feeding service conductors, and the service disconnect is at each building (with the OCPD).