Re: NON FUSED DISCONNECTS
In an exchange of private messages, I have learned that I had interpreted the question incorrectly. I am told that from some (unnamed and undescribed) upstream panel, conductors lead first to the disconnect, and then to this 225 amp panel that has a 225 amp main breaker. I am still not certain why the disconnect exists.
So the question becomes this: Can you have a 200 amp rated disconnect in series with that panel? The question is being asked because of the expectation that the load will not exceed 80% of that 225 amp breaker (i.e., 180 amps).
In view of my new understanding of the question, I will have to change my answer. No this is not acceptable. The breaker is permitted to carry 100% of it rated current, so long as it is not a "continuous load." But you can pass 224 amps through that 200 amp disconnect for 179 minutes, without violating the rule about breaker sizing. This would, however, violate the rule about operating a component (i.e., the disconnect) beyond its rating.