PE (always learning)
Senior Member
- Location
- Saint Louis
- Occupation
- Professional Engineer
Hey everyone,
Not trying to clog this forum with too many posts, I just have a big project I'm trying to complete and wanted to raise a question I had about the SCCR (Short Circuit Current Rating) of a non fusible disconnect when it is protected by a motor circuit protector (instantaneous only circuit breaker). I have a Siemens non fusible disconnect (Catalog #HNF363J) being fed by an Allen Bradley 140MG-G motor circuit protector located in a motor control center. I know that the fusible disconnect has an SCCR of 10 kA when protected by any UL listed circuit breaker, but is this the case when it's fed by a motor circuit protector that does not have the same UL listing as a circuit breaker?
Best Regards
Not trying to clog this forum with too many posts, I just have a big project I'm trying to complete and wanted to raise a question I had about the SCCR (Short Circuit Current Rating) of a non fusible disconnect when it is protected by a motor circuit protector (instantaneous only circuit breaker). I have a Siemens non fusible disconnect (Catalog #HNF363J) being fed by an Allen Bradley 140MG-G motor circuit protector located in a motor control center. I know that the fusible disconnect has an SCCR of 10 kA when protected by any UL listed circuit breaker, but is this the case when it's fed by a motor circuit protector that does not have the same UL listing as a circuit breaker?
Best Regards