Non-gfci for dedicated equipment in telecom

Status
Not open for further replies.

Crimsinx

New User
Location
Iowa
Occupation
Electrician
I'm looking for code that allows the use of a non-gfci 120v or 240v dedicated receptacle in remote telecom enclosures. We need to eliminate the gfci nuisance tripping for battery chargers. We will continue to have a gfci for personnel to use for their portable equipment.

Thank you for your help!
Brad, Iowa, USA
 
I think you need to start by looking at the article that you believe invokes a GFCI requirement in your installation. If there’s an exception, that’s where it will be.
 
If the receptacle is inside the enclosure I don't see that it needs GFCI protection.

What portable equipment is commonly used that isn't probably already battery powered?
 