Re: non grounded receptacles
With a properly wired circuit, if the hot or neutral between the outlet and the source gets broken (an open), the outlet stops working.
In this properly wired outlet if the ground becomes open the outlet still works with no grounding means, not a great situation but not immediately dangerous. No different from the old two wire circuits in use in many homes.
A second fault would need to happen before this in itself is dangerous.
Originally posted by g1051h:
What about bridging the neutral terminal to the green screw terminal on the receptacle to ground it. What are the problems with doing that?
An outlet wired this way, if this neutral/grounding conductor becomes open anywhere between the source (or bond depending on the condition of the grounding system) and the outlet the outlet will stop working but also the enclosure / case of whatever is plugged in becomes 'Hot'.
If a person now touches this enclosure and is grounded they will become the neutral conductor, they will be in series with the load.
To me this is immediately dangerous, along with the reasons of voltage drop and code rules makes using the neutral as the grounding means not an option.
[ March 21, 2004, 10:23 AM: Message edited by: iwire ]