I was thinking about this today, can EMT be used to extend a non grounded system? It is in a residential garage lighting outlet and the customer wants it extended to another point and it will be done with EMT. Now my concern is if the system is not grounded, how is this safe?
NOTE: No EGC being added.
It seems that 250.130(C) would disagree with you.
See above NOTE so 130(C) does not apply.
Exception No. 1: Metal enclosures and raceways for conductors
added to existing installations of open wire, knoband-
tube wiring, and nonmetallic-sheathed cable shall not
be required to be connected to the equipment grounding
conductor where these enclosures or wiring methods comply
with (1) through (4) as follows:
(1) Do not provide an equipment ground
(2) Are in runs of less than 7.5 m (25 ft)
(3) Are free from probable contact with ground, grounded
metal, metal lath, or other conductive material
(4)
Are guarded against contact by persons
He is extending not adding.
I assumed that it is not guarded.