Looking through old posts, can't find anything that sorts this out for me:
As I read Art. 500 and Art 501.10(B), ISA12.12 and ISA12.6 I get this:
If a non-incendive component or non-incendive equipment is installed per 501.10(B) it is approved for C1D2 without additional limitations on the field ciruit (assuming that all components of the field circuit are rated for the environments in which they are installed). This is because the field wiring methods in 501.10(B) are considered normally non-arcing. There is also no control drawing required for this method as the wiring is spec'd in 501.10(B)
If non-incendive field wiring of non-incendive field circuit techniques are used, the wiring does not have to be per 501.10(B), but there must be other protections available from other components to be approved for C1D2. These components must have marked non-incendive field wiring terminals and must be wired per a control drawing.
We are in the process on selecting components for our electrical panel (which will be in unclassified space) and want to make sure that we are not overdesigning since all of our selected components for the C1D2 location are listed as non-incendive.
As I read Art. 500 and Art 501.10(B), ISA12.12 and ISA12.6 I get this:
If a non-incendive component or non-incendive equipment is installed per 501.10(B) it is approved for C1D2 without additional limitations on the field ciruit (assuming that all components of the field circuit are rated for the environments in which they are installed). This is because the field wiring methods in 501.10(B) are considered normally non-arcing. There is also no control drawing required for this method as the wiring is spec'd in 501.10(B)
If non-incendive field wiring of non-incendive field circuit techniques are used, the wiring does not have to be per 501.10(B), but there must be other protections available from other components to be approved for C1D2. These components must have marked non-incendive field wiring terminals and must be wired per a control drawing.
We are in the process on selecting components for our electrical panel (which will be in unclassified space) and want to make sure that we are not overdesigning since all of our selected components for the C1D2 location are listed as non-incendive.