I am working in a Class 1 Div 2 area and have looked at Non-Incendive devices for this area, and have a few questions regarding the installation. The device in question is a temperature transmitter which is loop powered by 9.5 Vdc to 28 Vdc.
The transmitter Entity Parameters are: Vmax=28Vdc, Imax=100mA, C=0.037uF and L=0mH. I am not sure if the transmitter is powered, or if the device is truely just loop powered; however, I assume the following: If the transmitter has sperate power wires (4-Wires), if I fuse this circuit at or less than 100mA, I cover the Imax. Also, my power supply is rated at 24 Vdc, which I assume covers the Vmax. If my device is a true loop powered device (2-Wires) the analog module I am using is rated at 60mA @ 24Vdc, which I assume covers both the Vmax, and Imax of the entity parameters. If these answers are true, I still have the following questions:
Questions:
1. Can my device be powered by a power supply (24 Vdc), which powers all other non rated devices in my control system?
2. Can the wires for this device share the way wire way inside my control cabinet (MCP) and a wire duct above my MCP, prior to entering a single conduit to the rated device?
3. Can I simply recreate the manufacture's drawing into my control system drawing set, or does this OEM drawing get affixed to my drawing set?
4. If I can recreate the OEM drawing, what information has to be included?
Thanks for taking a look at my questions!
MIke
The transmitter Entity Parameters are: Vmax=28Vdc, Imax=100mA, C=0.037uF and L=0mH. I am not sure if the transmitter is powered, or if the device is truely just loop powered; however, I assume the following: If the transmitter has sperate power wires (4-Wires), if I fuse this circuit at or less than 100mA, I cover the Imax. Also, my power supply is rated at 24 Vdc, which I assume covers the Vmax. If my device is a true loop powered device (2-Wires) the analog module I am using is rated at 60mA @ 24Vdc, which I assume covers both the Vmax, and Imax of the entity parameters. If these answers are true, I still have the following questions:
Questions:
1. Can my device be powered by a power supply (24 Vdc), which powers all other non rated devices in my control system?
2. Can the wires for this device share the way wire way inside my control cabinet (MCP) and a wire duct above my MCP, prior to entering a single conduit to the rated device?
3. Can I simply recreate the manufacture's drawing into my control system drawing set, or does this OEM drawing get affixed to my drawing set?
4. If I can recreate the OEM drawing, what information has to be included?
Thanks for taking a look at my questions!
MIke