Non-Linear Load

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Student in class asked a question concerning non-linear loads and my answer leaned toward "yes" but that may not be correct.
Assume a 3 phase MWBC.
Phase A feeds load consisting entirely of non-linear lighting loads.
Phase B&C, however, feed non-linear loads.
Would the neutral be considered a CCC for derating purposes ??
 

jumper

Senior Member
Based on 310.15(B)(5)(c) I want to say no.

I do not see the MWBC as having a majority of non linear loads as only 1 phase of 3 has them.

Let me clarify my position:

If we assume that all three phases serve only L-N loads, Gus did not mention using any of the exceptions, then:

A phase is a nonlinear L-N load, with B and C being linear L-N loads.

I am not seeing how the shared neutral could have a majority of a load with harmonics causing it to be considered a CCC.

Am I missing something?
 
Last edited:

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
150826-0930 EDT

The original post indicated all three phases had non-linear loads, but the answers assumed that phases B & C were linear. I suspect the non-linear for B and C was a typo and should have been linear.

.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
150826-0930 EDT

The original post indicated all three phases had non-linear loads, but the answers assumed that phases B & C were linear. I suspect the non-linear for B and C was a typo and should have been linear.

.

Thank you ! I was a typo.. only one is non-linear, hence the question,
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Gus, in your OP you said you leaned toward "yes", why?

Ignorance ! :D
Simply because I felt the non-linear load would have an adverse effect on the neutral current
regardless of what was taking place on the other two phases. I pictured an unbalanced load adding to the non-linear situation resulting in a high neutral current but that is purely from an unlearned standpoint.
 

Carultch

Senior Member
Location
Massachusetts
Student in class asked a question concerning non-linear loads and my answer leaned toward "yes" but that may not be correct.
Assume a 3 phase MWBC.
Phase A feeds load consisting entirely of non-linear lighting loads.
Phase B&C, however, feed linear loads.
Would the neutral be considered a CCC for derating purposes ??

Out of ignorance, I would be conservative when in doubt. If this were a practical in-the-field example, I would count the neutral as a CCC in this example for derating purposes.

Ok to do that for practical examples in the field, but gotta be careful when taking an exam.

And unfortunately, I see this rule as kind of vague. If I measure every detail of the loads with an oscilliscope, what measurable characteristic should I look for to know whether or not "a major portion of the load is nonlinear"?
 
Last edited:

Carultch

Senior Member
Location
Massachusetts
Ignorance ! :D
Simply because I felt the non-linear load would have an adverse effect on the neutral current
regardless of what was taking place on the other two phases. I pictured an unbalanced load adding to the non-linear situation resulting in a high neutral current but that is purely from an unlearned standpoint.

As I understand it, the intent of this rule is to remind us that harmonic currents may not "cancel out" on the neutral conductor. Especially the 180 Hz third harmonics, and its larger multiples thereof, which accumulate instead of cancel, onto the neutral.

The idea is whether or not the four wires (ABC & N) all can generate more heat collectively, than the maximum possible heat generated by only the phase conductors, at full ampacity. And if that is the case, neutral should be counted.
 

Smart $

Esteemed Member
Location
Ohio
Okay, I see non-linear typo has been covered, but you did not mention amount of loading on each phase. 50% is based on total load. If A were 16A while B & C were both 7.5A, the neutral would be considered a CCC. Please note that circuit loading vs. circuit ampacity does not enter the determination.
 

Carultch

Senior Member
Location
Massachusetts
Okay, I see non-linear typo has been covered, but you did not mention amount of loading on each phase. 50% is based on total load. If A were 16A while B & C were both 7.5A, the neutral would be considered a CCC. Please note that circuit loading vs. circuit ampacity does not enter the determination.

Is it realistic to calculate this in terms of KVA in total?

If KVA_nonlinear / KVA_total is greater than 50%, then neutral counts as a CCC. No matter how the linear and non-linear is distributed among the phases.

Also, once a load classifies as nonlinear, should its entire KVA be counted in the nonlinear total, no matter what the degree of non-linearity?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Smart: This was a question asked by a student in a class so use numbers you wish :)
In his description, Phase A would be a fully loaded non-linear load supplying lighting, Phase B & C are linear supplying receptacles.
Assuming he is needing to derate for ambient, fill, etc., he asked does the neutral count.
 

Carultch

Senior Member
Location
Massachusetts
Smart: This was a question asked by a student in a class so use numbers you wish :)
In his description, Phase A would be a fully loaded non-linear load supplying lighting, Phase B & C are linear supplying receptacles.
Assuming he is needing to derate for ambient, fill, etc., he asked does the neutral count.

I sure hope your student doesn't write the exam questions in his future. Please thank him for offering us the interesting challenge.

"Linear supplying receptacles". Not sure that this is as fixed of a load nature as one might think. In the past, there used to be a lot more linear loads, like motors and incandescent lighting. Now that technology has changed, we've reduced the KVA and increased the nonlinearity of a lot of receptacle loads (fluorescent lights, LEDs, power supplies, computers).
 

Haji

Banned
Location
India
Smart$:
I think, if the neutral ampacity is not exceeded, nonlinear load may exceed 50%. Only when the neutral is loaded to its full ampacity, does the restriction on the part of the nonlinear load not exceeding 50% apply. What do you think based on the code? Thanks.
 

Smart $

Esteemed Member
Location
Ohio
Is it realistic to calculate this in terms of KVA in total?

If KVA_nonlinear / KVA_total is greater than 50%, then neutral counts as a CCC. No matter how the linear and non-linear is distributed among the phases.

Also, once a load classifies as nonlinear, should its entire KVA be counted in the nonlinear total, no matter what the degree of non-linearity?
Being realistic has little to no influence on Code compliance.

Your second statement is how I interpret the written word.

Level of calculation scrutiny is not dictated by NEC. That duty falls upon AHJ... :D
 

Smart $

Esteemed Member
Location
Ohio
Smart: This was a question asked by a student in a class so use numbers you wish :)
In his description, Phase A would be a fully loaded non-linear load supplying lighting, Phase B & C are linear supplying receptacles.
Assuming he is needing to derate for ambient, fill, etc., he asked does the neutral count.
Tell him that should Phase B & C loads be entirely linear, the neutral would not count.

Then tell him with Phase B & C supplying receptacles their loads are unknown. The load served at any point in time could range from entirely linear to entirely nonlinear. Then ask the student to make the wisest choice... :angel:
 

Smart $

Esteemed Member
Location
Ohio
Smart$:
I think, if the neutral ampacity is not exceeded, nonlinear load may exceed 50%. Only when the neutral is loaded to its full ampacity, does the restriction on the part of the nonlinear load not exceeding 50% apply. What do you think based on the code? Thanks.
With nonlinear loads combining on the neutral at a level somewhere between the arithmetic sum and a typical vector sum, how do you determine whether the neutral ampacity is exceeded before you put it in?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Can anyone show me a documented case of neutral conductor overheating from non-linear loads in someplace other than a data center?

This is a case where almost all of the published information on the problems that may be caused by non-linear loads come from the people that have something to sell you to solve the problem.
 