Good evening all nice to be here,
I have a long winded question but I need some peer feedback as I stand alone in my thinking at this point. I reviewed a dwg. that shows a 15K/3000 A MV transformer with local 480/277 v disconnect rated 3000A feeding a 3000amp switchboard approx.125 ft. away.Transformer is outside, conduit rack route is through non climate controlled building back outside to outdoor 3000 amp SWBD. I am in MD/ DC area where summer temps frequently reach above 86 °F. The switchboard is feeding all Battery Elec. Bus charging which are non linear loads.Dwg. shows 8-4" rgs conduits with 4- 500 kcm. I say because of table 310.15(B)(2)(A) and 310.15(B)(2)(C) it should be 5-700 kcm in 5" rgs. One last note no ground shown in conduits. What say you guys?
I have a long winded question but I need some peer feedback as I stand alone in my thinking at this point. I reviewed a dwg. that shows a 15K/3000 A MV transformer with local 480/277 v disconnect rated 3000A feeding a 3000amp switchboard approx.125 ft. away.Transformer is outside, conduit rack route is through non climate controlled building back outside to outdoor 3000 amp SWBD. I am in MD/ DC area where summer temps frequently reach above 86 °F. The switchboard is feeding all Battery Elec. Bus charging which are non linear loads.Dwg. shows 8-4" rgs conduits with 4- 500 kcm. I say because of table 310.15(B)(2)(A) and 310.15(B)(2)(C) it should be 5-700 kcm in 5" rgs. One last note no ground shown in conduits. What say you guys?