I frequently make my own expansion couplings/slip riser by using different sizes of PVC. For example a 2 1/2 schedule 40 fits nicely over 2". In fact the factory slip risers are exactly just a piece of two and a half schedule 40 with the other end shrunk down and a 2-inch TA on it. So I got called on this and was told I needed to use a listed expansion fitting. Here was my response:
Ok XYZ thanks. We will have to agree to disagree on this. I see nothing in the NEC prohibiting my method. While certainly I agree that 352.10 requires PVC fittings to be listed,. I contend that all of these fittings are listed, and there is no requirement that A fitting be listed for the purpose. Also note there are other ways to comply with the expansion requirement besides an expansion coupling. See 300.5(J), particularly the informational note that follows.
What does the group think?
Ok XYZ thanks. We will have to agree to disagree on this. I see nothing in the NEC prohibiting my method. While certainly I agree that 352.10 requires PVC fittings to be listed,. I contend that all of these fittings are listed, and there is no requirement that A fitting be listed for the purpose. Also note there are other ways to comply with the expansion requirement besides an expansion coupling. See 300.5(J), particularly the informational note that follows.