Non Metallic Floor Box in Health Care Facility

Status
Not open for further replies.
I will be installing floor boxes in a Chiropractic office. According to 517.13 wiring method has to be in metal raceway or sheath.
I was planning on using PVC schedule 40 to a non metallic floor box in the concrete slab.
Would this be in violation of 517.13?
If so would it be acceptable to pull HCF mc in the PVC but I don't know how I would terminate the jacket for redundant ground
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Seemingly you have identified the problem yourself with the HCF termination. In addition, if it's a ground level slab the interior of the PVC would be a wet location and the HCF, if usable, would need to be jacketed.
 
That is interesting. I did a Chiropractor office a few years ago and that was the first thing the inspector ask, "you are using HCF mc right?" which I did. I will check with the AHJ. I would think if they are using electrical devices to treat patients it would be considered a Health Care Facility.
 