I doubt it unless inside the enclosure is a wet location.Is it an NEC code violation to use non- outdoor rated wire nuts inside an outdoor rated enclosure mounted outdoors?
Sent from my SM-G930V using Tapatalk
Is it an NEC code violation to use non- outdoor rated wire nuts inside an outdoor rated enclosure mounted outdoors?
Sent from my SM-G930V using Tapatalk
Is it an NEC code violation to use non- outdoor rated wire nuts inside an outdoor rated enclosure mounted outdoors?
Sent from my SM-G930V using Tapatalk
300.5 Underground Installations.
(B) Wet Locations. The interior of enclosures or raceways installed underground shall be considered to be a wet location. Insulated conductors and cables installed in these enclosures or raceways in underground installations shall be listed for use in wet locations and shall comply with 310.8(C). Any connections or splices in an underground installation shall be approved for wet locations.