Context - I'm in a situation where an EPO for a datacenter is getting removed by a project due to the distribution board where all of the shunt trips were getting removed.
In addition to this, a bunch of data cable was to be installed during the outage. The datacenter manager incorrectly purchased non plenum rated cable that is to be run under the raised floor. Below this raised floor is considered a plenum in this case as it is pressurized to support airflow to the datacenter.
None of this data cable is to be run in a plenum rated fully metal enclosed raceway
We are trying to comply with 645.10 (B). I believe we meet all the requirements except (5):
"cables installed under a raised floor, other than branch circuit wiring, and power cords are installed in compliance with 645.5(E)(2) or (E)(3), or in compliance with Table 645.10(B)."
Table 645.10(B) refers to the general requirements for data cables (Article 800). In short the cables will need to be enclosed in metal raceways (essentially refers to article 300.22 (C)). Doesn't apply to us in this case due to the lack of enclosed raceways.
Article 645.5(E)(2) parts (4) and (5) say data cables in a below raised floor plenum can only be non-plenum rated "where the air space under a raised floor is protected by an automatic fire suppression system".
This datacenter has an automatic fire suppression sprinkler system at the ceiling of the datacenter. it does not have any sprinkler heads below the raised floor, but there are perforated tiles used for airflow.
My ultimate question being, does this count as protecting the air space below the raised floor?
My hunch says no. The code seems to imply what I believe as well. Unfortunately, I cannot find anything across several code books that explicitly defines that the protection above the raised floor can or cannot be considered for protection below the raiser floor.
The best I found was NFPA 13 article 8.15.1.2.2.1 which says (paraphrasing) that concealed spaces of noncombustible and limited-combustible construction, even with small openings such as those used as return air for a plenum, with limited access and not permitting occupancy or storage of combustibles shall not require sprinkler protection.
non-plenum rated cables would be the combustibles making this exception untrue for us. however this still doesn't explicitly state what I'm looking for as some could still interpret this space as protected from the above system.
Side note - as far as I understand, keeping the EPO in place would still not waive the requirement to have either plenum rated cables, or sufficiently protected non-plenum rated cables as defined in 645.5(E)(2) or 300.22(C) correct?
Basically the only time non-plenum rated cable can be under a raised floor plenum, is if it is in a plenum rated conduit per 300.22(C), or one of the exceptions in 645.5(E)(2)(4) w/ automatic fire suppression system protection (assuming all of 645.4 is also met).
In addition to this, a bunch of data cable was to be installed during the outage. The datacenter manager incorrectly purchased non plenum rated cable that is to be run under the raised floor. Below this raised floor is considered a plenum in this case as it is pressurized to support airflow to the datacenter.
None of this data cable is to be run in a plenum rated fully metal enclosed raceway
We are trying to comply with 645.10 (B). I believe we meet all the requirements except (5):
"cables installed under a raised floor, other than branch circuit wiring, and power cords are installed in compliance with 645.5(E)(2) or (E)(3), or in compliance with Table 645.10(B)."
Table 645.10(B) refers to the general requirements for data cables (Article 800). In short the cables will need to be enclosed in metal raceways (essentially refers to article 300.22 (C)). Doesn't apply to us in this case due to the lack of enclosed raceways.
Article 645.5(E)(2) parts (4) and (5) say data cables in a below raised floor plenum can only be non-plenum rated "where the air space under a raised floor is protected by an automatic fire suppression system".
This datacenter has an automatic fire suppression sprinkler system at the ceiling of the datacenter. it does not have any sprinkler heads below the raised floor, but there are perforated tiles used for airflow.
My ultimate question being, does this count as protecting the air space below the raised floor?
My hunch says no. The code seems to imply what I believe as well. Unfortunately, I cannot find anything across several code books that explicitly defines that the protection above the raised floor can or cannot be considered for protection below the raiser floor.
The best I found was NFPA 13 article 8.15.1.2.2.1 which says (paraphrasing) that concealed spaces of noncombustible and limited-combustible construction, even with small openings such as those used as return air for a plenum, with limited access and not permitting occupancy or storage of combustibles shall not require sprinkler protection.
non-plenum rated cables would be the combustibles making this exception untrue for us. however this still doesn't explicitly state what I'm looking for as some could still interpret this space as protected from the above system.
Side note - as far as I understand, keeping the EPO in place would still not waive the requirement to have either plenum rated cables, or sufficiently protected non-plenum rated cables as defined in 645.5(E)(2) or 300.22(C) correct?
Basically the only time non-plenum rated cable can be under a raised floor plenum, is if it is in a plenum rated conduit per 300.22(C), or one of the exceptions in 645.5(E)(2)(4) w/ automatic fire suppression system protection (assuming all of 645.4 is also met).