Non Power Limited FA circuits/devices

Status
Not open for further replies.

tschooley

New member
I am looking for examples of Non Power Limited Fire Alarm circuits/devices that meet the requirements of NEC 760.

I have a presentation on the 17th of December. Can anyone offer any insight?

Thanks,

Troy Schooley
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Non Power Limited FA circuits/devices

They would be a line voltage fire alarm with 120v bells and devices. they are probably few and far betwee.
 

fyretek

Member
Re: Non Power Limited FA circuits/devices

Yeah and thank god for that..woot... all hail the addressable system yeahhh hehehe. god i hated working on series bell ckts. here is a link not sure if it helps you for a show and tell or not but here it is

web page
 

ron

Senior Member
Re: Non Power Limited FA circuits/devices

From what I understand, many FACP power supplies can be purchased either 24V power limited or 24V non-power limited. Depends on the application.
 

ron

Senior Member
Re: Non Power Limited FA circuits/devices

fyretek,
Regarding your link to the CI cable, have you had much call for it? Generally it has very limited use, and many argue that there is no code requirement for it.

BTW, I specify its use on many of my larger buildings I design.
 