Non separately derived generator grounding question

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have non separately derived generator with all 3 poles ATS. However, I have drawing that shows generator grounding detail as below.

I am confused how can non separately derived system have grounding as shown below snapshot. Would this be allowed based off of NEC 2017? If yes then which NEC 2017 Article?

8101c4722081fe1b58bb1a5b628abe60.jpg
 
It's not clear to me that the diagram shows system grounding, i.e. connecting the electrode to the grounded conductor/neutral. If it's just earthing the generator frame and housing then that could be to satisfy 250.32 or done under 250.54 if the manufacturer wants the generator frame and housing grounded. To say if there's anything wrong we need more info on what the 'generator ground point' (item 6) connects to, and whether neutral-to-ground bonding can be installed or removed in the generator.
 
You say 3 pole, is this a single phase, or 3 phase generator?

I see specs where the owner wants additional ground rods and earthing at the generator, even though it’s not necessary or required.
 
I agree with the others. It appears that there is no connection to the neutral so there is no issue with bonding the frame or the enclosure to an electrdoe.
 
I thought generators always needed their case to be connected to a grounding electrode.

But now I can't find why I thought that.

Maybe it was for static or similar for the gas tank?
 