I have non seprately derived emergency generator. The generator has three breakers that feed three ATS downstream but no main breaker.
One of the ATS call it ATS-3 is fed from service switchboard feeder breaker. The service switchboard has main breaker and 6 feeder breakers.
Here is the thing the ATS-3 feeds 480V transformer primary which does not require neutral.
However neutral is not switched in ATS-3 and generator is not separately derived. How would one address this, neutral has to be brought to the ATS-3 from service switchboard feeder breaker and generator feeder breaker?
One of the ATS call it ATS-3 is fed from service switchboard feeder breaker. The service switchboard has main breaker and 6 feeder breakers.
Here is the thing the ATS-3 feeds 480V transformer primary which does not require neutral.
However neutral is not switched in ATS-3 and generator is not separately derived. How would one address this, neutral has to be brought to the ATS-3 from service switchboard feeder breaker and generator feeder breaker?