Hi all, I need help understanding the proper connection of a generator in an existing system.
Existing system
The existing system has a Service Panel Wye (480V-277V, 3ph, 4w) where the Neutral and ground are bonded. Downstream feeders are all 3W+EGC; there are no 277V loads, so neutral is not required.
Some of these feeders supply the normal source input of 3-pole ATSs.
The existing generators feed a Switchboard, 3phase 3w (no neutral). The feeder coming from the Generator to the SWBD is 3ph + EGC.
Then, the ATSs are supplied from the SWBD (backup source) via 3W+EGC feeders.
Generator and Questions
I understand this is a NON separately derived system due to the 3pole ATSs and the feeders coming from the service and generators which are 3W. is this correct?
The generator has a CB in its cabinet, so the G conductor from the generator to the SWBD is an Equipment Grounding Conductor EGC. Is this correct?
If there is no neutral conductor from the generator connected to the Service neutral, my interpretation is that the system is floating (code violation for 480V?). Is that correct?
What should be the proper way to design the grounding and neutral treatment of the generator?
Is the neutral and ground bond required at the generator? supply side body jumper? GEC?
If the EGC from the generator is connected to the neutral point at the generator, is that a code violation since this is a Non sep. derived system? Note that the ground is connected to the frame.
Thank you so much!
Existing system
The existing system has a Service Panel Wye (480V-277V, 3ph, 4w) where the Neutral and ground are bonded. Downstream feeders are all 3W+EGC; there are no 277V loads, so neutral is not required.
Some of these feeders supply the normal source input of 3-pole ATSs.
The existing generators feed a Switchboard, 3phase 3w (no neutral). The feeder coming from the Generator to the SWBD is 3ph + EGC.
Then, the ATSs are supplied from the SWBD (backup source) via 3W+EGC feeders.
Generator and Questions
I understand this is a NON separately derived system due to the 3pole ATSs and the feeders coming from the service and generators which are 3W. is this correct?
The generator has a CB in its cabinet, so the G conductor from the generator to the SWBD is an Equipment Grounding Conductor EGC. Is this correct?
If there is no neutral conductor from the generator connected to the Service neutral, my interpretation is that the system is floating (code violation for 480V?). Is that correct?
What should be the proper way to design the grounding and neutral treatment of the generator?
Is the neutral and ground bond required at the generator? supply side body jumper? GEC?
If the EGC from the generator is connected to the neutral point at the generator, is that a code violation since this is a Non sep. derived system? Note that the ground is connected to the frame.
Thank you so much!