ctaylo360860
Senior Member
- Location
- colorado
- Occupation
- ME
Hoping to get some more help on this genset install.... this would have to be with sizing my conductors from my genset to my Automatic transfer Switch...
nameplate on genset motor is:
kw-276 volts-208/416
kva-364 amps 958/479
nameplate on genset alternator:
volts-277/480
amps-381.6
kva-312.5
So my genset has a 300a breaker, I planned on sizing my conductors big enough for 400A between genset and Service entrance rated ats. I am doing this incase in the future it is needed to install a larger 400a breaker. I am looking at running 5 wires in a piece of liquid tight flexible metal conduit between ATS and GENSET. if I do this I will have to derate those conductors to 80% since I'm over four current carrying conductors? so if I were planning to upsize to 400amps instead of 300amps id actually have to run 250kcmill copper paralleled to get 400amps. 255A x 80% = 204amps... 2 paralleled conductors = 408amps... with that said Ill have to have two pieces of 3" liquid tight flexible metal conduit with five conductors in each raceway... my lugs are 1=600kcmill or 2-250kcmill. I'm wondering if I should just size the conductors to the 300A breaker because its going to be unlikely they will add more load to the generator, and the 300A breaker is sufficient to carry the load they have right now.... Also I'm wondering if anyone has any ideas that i can easily install and uninstall the genset. the genset is used to keep tarps for corn bunks on during a power outage, but once the bunks are empty I will be uninstalling and storing generator. I was thinking something like a powertite 400amp pin and sleeve cable connectors and plug and some 600mcm so cord with 5 conductors ... the only problem is I cant find any cord that big nor can I find a pin and sleeve that will take 3 grounded conductors, 1 grounded conductor, and a e.g.c. . I need to run 5 conductors in each raceway since my genset is a non separately derived system, and I need isolate grounded conductor from equipment groundings conductors and frame of genset... any and all help is greatly appreciated!!!! THANKS IN ADVANCE!
nameplate on genset motor is:
kw-276 volts-208/416
kva-364 amps 958/479
nameplate on genset alternator:
volts-277/480
amps-381.6
kva-312.5
So my genset has a 300a breaker, I planned on sizing my conductors big enough for 400A between genset and Service entrance rated ats. I am doing this incase in the future it is needed to install a larger 400a breaker. I am looking at running 5 wires in a piece of liquid tight flexible metal conduit between ATS and GENSET. if I do this I will have to derate those conductors to 80% since I'm over four current carrying conductors? so if I were planning to upsize to 400amps instead of 300amps id actually have to run 250kcmill copper paralleled to get 400amps. 255A x 80% = 204amps... 2 paralleled conductors = 408amps... with that said Ill have to have two pieces of 3" liquid tight flexible metal conduit with five conductors in each raceway... my lugs are 1=600kcmill or 2-250kcmill. I'm wondering if I should just size the conductors to the 300A breaker because its going to be unlikely they will add more load to the generator, and the 300A breaker is sufficient to carry the load they have right now.... Also I'm wondering if anyone has any ideas that i can easily install and uninstall the genset. the genset is used to keep tarps for corn bunks on during a power outage, but once the bunks are empty I will be uninstalling and storing generator. I was thinking something like a powertite 400amp pin and sleeve cable connectors and plug and some 600mcm so cord with 5 conductors ... the only problem is I cant find any cord that big nor can I find a pin and sleeve that will take 3 grounded conductors, 1 grounded conductor, and a e.g.c. . I need to run 5 conductors in each raceway since my genset is a non separately derived system, and I need isolate grounded conductor from equipment groundings conductors and frame of genset... any and all help is greatly appreciated!!!! THANKS IN ADVANCE!