See 411.4
411.4 Listing Required. Lighting systems operating at
30 volts or less shall comply with 411.4(A) or 411.4(B).
Class 2 power sources and lighting equipment connected to
Class 2 power sources shall be listed.
(A) Listed System. Lighting systems operating at 30 volts
or less shall be listed as a complete system. The luminaires,
power supply, and luminaire fittings (including the exposed
bare conductors) of an exposed bare conductor lighting system
shall be listed for the use as part of the same identified
lighting system.
(B) Assembly of Listed Parts. A lighting system assembled
from the following listed parts shall be permitted:
(1) Low-voltage luminaires
(2) Low-voltage luminaire power supply
(3) Low-voltage luminaire fittings
(4) Cord (secondary circuit) for which the luminaires and
power supply are listed for use
(5) Cable, conductors in conduit, or other fixed wiring
method for the secondary circuit
The luminaires, power supply, and luminaire fittings
(including the exposed bare conductors) of an exposed bare
conductor lighting system shall be listed for use as part of
the same identified lighting system.
Was it comprised of the above?