Non-ventilated in that size will need to be oil filled (e.g. secondary unit substation transformer) and 150KVA would be an odd size, probably would have to go to 300KVA. You can more readily get 75KVA in encapsulated type but that is about the maximum size. In a pinch you could operated two 75 KVA in parallel, just make sure the impedances are very, very close to the same.
What is the reason for non-ventilated? Perhaps there are other alternatives if we had more details.