Non-water-tight connector used on Meter Socket?
davedottcom
Is a non-water-tight SE Clamp Connector permitted to be used on the side K.O. of an outdoor Meter Socket?
Maybe. Is the KO above the live parts?
312.2 Damp and Wet Locations. In damp or wet loca-
tions, surface-type enclosures within the scope of this ar-
ticle shall be placed or equipped so as to prevent moisture
or water from entering and accumulating within the cabinet
or cutout box, and shall be mounted so there is at least
6-mm ( 1/4 -in.) airspace between the enclosure and the wall
or other supporting surface. Enclosures installed in wet lo-
cations shall be weatherproof. For enclosures in wet loca-
tions, raceways or cables entering above the level of unin-
sulated live parts shall use fittings listed for wet locations