Re: Nonhazardous ansthetizing locations
Roger:
I described the location as "other-than-hazardous."
Section 517-63(b) provides the following:
"Branch circuits supplying only listed, fixed, therapeutic and diagnostic equipment, permanently installed above the hazardous location and in other-than-hazardous locations, shall be permitted to be supplied from a normal grounded service, single or three-phase system provided the following:"
This appears to be a permissive rule that allows specific types of fixed, listed equipment to be supplied from a grounded service anywhere in an other-than-hazardous anesthetizing location.
Does this mean that portable equipment is not permitted to be supplied from a grounded service? I can't find any specific prohibition against this. So what is purpose of this permissive rule?
[ September 21, 2005, 12:10 PM: Message edited by: rbb ]