The company I work for does not use NonIncendive devices. These devices are tested under Normal condition for Class 1 DIV 11. We only install devices tested under fault condition ex. I.S. or Explosion Proof.
Recently we have found field devices install in this plant that have an NI rating. We were discussing the safey aspects of this device which led to the control drawing for this switching device. The way we read ISA 12.12 or FM Class 3611 a control dwg is required for installation. The manufacture says a control drawing is not necessay for a device with the rating marked on the device. We think this statement is wrong. The control drawing should show the install procedure and the limit form our equipment to the device. Example: Power limit, current limits, voltage limits.
How do you interpret the code? We have remove the devices from our plant.
Recently we have found field devices install in this plant that have an NI rating. We were discussing the safey aspects of this device which led to the control drawing for this switching device. The way we read ISA 12.12 or FM Class 3611 a control dwg is required for installation. The manufacture says a control drawing is not necessay for a device with the rating marked on the device. We think this statement is wrong. The control drawing should show the install procedure and the limit form our equipment to the device. Example: Power limit, current limits, voltage limits.