Can we run both normal (N) and emergency (E) lighting circuits to the same lighting control panel? (there is a divider inside lighting control panel to separate N/E lighting circuits)
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Yes. I have done that recently. The manufacturer had a listing that took credit for an internal barrier for separating Normal relays from Emergency relays, and for separating the wiring as well.
 

iwire

Moderator
Staff member
Location
Massachusetts
I agree with Mr Beck but will add that the design of the lighting control panel must be such that the emergency lighting will always come if there is a power failure regardless of any other commands, inputs or programing etc.
 

anbm

Senior Member
Location
TX
Occupation
Designer
How do we comply with 700.9(B) or 517.30(C)(1)? Because a relay panel is still a single cabinet.
 