Article 700.9 (B)of the NEC states "...emergency loads shall be kept entirely independent of all other wiring and equipment, unless otherwise permitted in (1) through (4): Specifically, (3)"Wiring from two sources in a common junction box, attached to exit or emergency luminaires (lighting fixtures). Based on this language is it acceptable to run normal and emergency wiring for a 2'x4' light fixture that contains 2 lamps on emergency and 2 lamps on normal within the same ballast channel? I say yes but some contractors, engineers, and manufacturers differ in there interpretation. Any advise would be appreciated.