Does article 517 clearly state that lighting on the normal branch must be provided at patient bed locations?
Edit.... "In other words ether a critical branch and a normal branch 0r two critical branches must serve outlets at each patient bed location. Does that also include a requirement that lighting installed at patient bed locations must be served by two required branches."....
NFPA 99
6.3.2.2.11.1 One or more battery-powered lighting units shall be provided within locations
where deep sedation and general anesthesia is administered.
6.3.2.2.11.3 The sensor for units shall be wired to the branch circuit(s) serving general lighting
within the room.
Edit.... "In other words ether a critical branch and a normal branch 0r two critical branches must serve outlets at each patient bed location. Does that also include a requirement that lighting installed at patient bed locations must be served by two required branches."....
NFPA 99
6.3.2.2.11.1 One or more battery-powered lighting units shall be provided within locations
where deep sedation and general anesthesia is administered.
6.3.2.2.11.3 The sensor for units shall be wired to the branch circuit(s) serving general lighting
within the room.