Hello folks, just looking to get some verification on voltage drop.
When I calculate the voltage drop of the Feeder going to an apartment in a multifamily building I am using 2% as my permitted voltage drop, along with the connected load, not the demand load.
As I see it, using 2% and the connected load, I should capture the worst case scenario.
I'm sure the demand load would give a more practical result, but I can't seem to find any information as to which load should be used.
Also, I would like to confirm the fact that I use the voltage drop permitted for feeders which is 2%; as others I've seen use 3% on these runs.
Thanks
Kevin
When I calculate the voltage drop of the Feeder going to an apartment in a multifamily building I am using 2% as my permitted voltage drop, along with the connected load, not the demand load.
As I see it, using 2% and the connected load, I should capture the worst case scenario.
I'm sure the demand load would give a more practical result, but I can't seem to find any information as to which load should be used.
Also, I would like to confirm the fact that I use the voltage drop permitted for feeders which is 2%; as others I've seen use 3% on these runs.
Thanks
Kevin