Why we cannot use 2 1/2" Conduit - HDPE, Wave-Rib Flexible Continuous Duct (Coiled/Reeled), schedule 40, red in color, rated for direct burial and 90 C conductor that the utility company use for service entrance conductors for a subpanel feed?
I installed the above from the pedestal to a 200 amps service and I asked the inspector to use the left over (about 30') to run it - underground, with the proper risers - to a 100 amps subpanel. I know it is not listed, but it sound burocratic that it can be use to run 4.0 AL SE and not copper feeders or any conductors for the subpanel. Inspector stated that soft core must not be use??????
I installed the above from the pedestal to a 200 amps service and I asked the inspector to use the left over (about 30') to run it - underground, with the proper risers - to a 100 amps subpanel. I know it is not listed, but it sound burocratic that it can be use to run 4.0 AL SE and not copper feeders or any conductors for the subpanel. Inspector stated that soft core must not be use??????