Not sure how to size this equipment breaker. 6|89T Edge Sander

Merry Christmas

Cartoon1

Senior Member
Location
Florida
Occupation
Electrical Engineer
Hello, I'm trying to figure out how to size electrical for a Sander machine (6|89T Edge Sander). It says 1.5HP 110V 18AMP and when i look at its manuals it shows a receptacle 20amp type to be used. Not sure if this 18AMP FLA or Startup. But lets assume it is 18AMP FLA. Can you use a 20A rated receptacle with a 20A breaker since this will exceed the 80% of a 20amp breaker?

Now, if i do 18*125% to size cable then i will end up with a 22.5A for the cable and at least a 25A breaker and a special type receptacle. But they show a typical 20A plug as one of their options.

If i use the HP to size it only 1.5HP, then i'm looking at something like 20FLA with a recommended 40A breaker based on my square d motor data calculator. again, with a different plug and special receptacle.

So what would be a the right way to size the electrical for something like this?

Thank you
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Does it have a cord an plug on it from the manufacturer? If so just use that to size the branch circuit. With a FLA of 18 amps you could use a 20 amp circuit if the unit will start. No need to add 125%.
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
Does it have a cord an plug on it from the manufacturer? If so just use that to size the branch circuit. With a FLA of 18 amps you could use a 20 amp circuit if the unit will start. No need to add 125%.
If the sander is cord and plug connected, portable not fastened in place, wouldn't 210.23 (1) apply. 18 amps on a 20 amp rated circuit would exceed 80% of the branch circuit ampere rating.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the sander is cord and plug connected, portable not fastened in place, wouldn't 210.23 (1) apply. 18 amps on a 20 amp rated circuit would exceed 80% of the branch circuit ampere rating.
That only applies to multiple outlet circuits {210.23}. A 20 amp individual branch circuit with a single receptacle can be loaded to 20 amps.
 