Yes, if the wires all have insulation that is good enough for at least 480 volts. But since most wire has 600 volt insulation, that should be easy to meet. Reference 300.3(C)(1). Be aware of the derating requirements for having more than three current-carrying conductors in the same conduit. Reference 310.15(B)(3).