Not sure about the Ground lug on the outside of the Generator Frame...here's the set up:
1)The Auto Transfer switch does Not switch (Or Bond) the grounds & neutrals.
(According to our good friend, Mr. Holt, if the Transfer switch does Not open the grounded neutral conductor the Generator is Not a seperately derived system)
2)The (70Amp) generator does Not bond the grounds and neutrals either.(Bond is from Ground lug to frame only)
So far so good!
3) The #10 Ground (pre-wired whip from factory) runs from the Generator to the transfer switch. Transfer Switch is grounded from the main panel.
Editted to add: This transfer switch is also a load center. (grounds and neutrals still seperate at this point!)
(Grounds & Neutrals bonded in Main Panel only)
So far so good still!
4)There is a lug on the outside of the Generator for grounding the frame to something else!
But this would create a parallel ground since it is already grounded by the #10 in the "whip".
Is this #10 (pre-wire) ground from the Auto/transfer switch all that is needed for a 15K Generator???
I can't figure out how the ground lug on the outside of the Gen. could be utilized without creating a paralleled ground.
Dave