I am confused. Note: after 250.34 reads:A portable or vehicle-mounted generator suppling fixed wiring for a
premises must be grounded (connected to earth) and bonded in accordance with 250.30 for separately systems
and 250.35 for nonseparately derived systems.
Maybe I am misunderstanding how this is written. My understanding is 250.30 would require the neutral to be
boned at the generator, and 250.35 would not want the neutral to be bonded at it.
Also what happens if a portable generator is used to supply a premises during a power outage using cord and receptacles (Gentran) to connect to the service, and removes the plug connection when power is restored, and uses the generator as portable, now IMO the neutral would have to be bonded.
Explanation please am I missing something?
Thanks