Does this article pertain to a feeder for a subpanel in a residential application I would think not but I'm not 100% sure.
My take is that the answer is "no" as Code asked it: "...a feeder for a subpanel..." This clearly refers to the service feeders: "the main power feeder to each dwelling unit", and not sub-panel feeders.Originally posted by codeunderstanding:
Does this article pertain to a feeder for a subpanel in a residential application I would think not but I'm not 100% sure.
This is not what the NEC is saying. It allows one wire size smaller for the service conductors that run from the drop/laterals all the way to the first lighting, branch circuit panel board(s). The (s) is where you have installed two parallel panels like off a 320 meter. Any panel after the first lighting/branch circuit panel has to have the full sized wire to it.By Frank: Sub Panel: Any and all panels that are not Main Panels,(see main panels)
For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit Panelboard(s)