Richardh247
Member
- Location
- Paris, TX
I think I am just over-thinking this but I am at wit's end here. I recently bid (and won) a job that calls for a 3-phase, 400A, 480/277 Wye service. Connected to that was to be a 3-phase, 200A, 208/120 Wye to service the general receptacle and exhaust fan loads. Simple stuff.
I visited the site to finalize some measurements for the lateral primary run and, while there, I noticed that the exhaust fans were in and I took a peek. They are 1/2hp 240V with an FLA of 3.3 or 6.6 if connected to 120V. While there, I was also informed that I needed to add a "typical" (his words) receptacle for a welder - standard 240V., 50A supply.
This throws all of my calcs. If those fans were 230V. listed I might, and I do mean might, take a chance on a 208V supply. But with a plate rating of 240V I am not comfortable chancing it.
All of this swimming around in my head for the last couple of days has done nothing but confuse me. I know the answer is drop dead simple, but it isn't coming to me.
So...
That the MDP is 480, 3-phase in a Wye configuration from the CTs, I have two options that I can see:
1. 208V 3-phase Wye secondary off a 45KVA xfmr and hook up the exhaust fans to single phase 120 and make him buy a welder to accommodate my service;
2. A Wye/Delta 240V 3-phase xfmr, also 45KVA, center tapped for some 2-pole 240 and a 208V stinger that will never be used anywhere for anything and will unbalance the secondary panel.
One of the overriding issues I have, and I'm hoping for some input on this, is that the bids are in. Obviously I will have to recalculate everything and resubmit my price, but I want to make sure his expansion needs are covered to the best of my ability without soaking the material budget with needless excess. This job has no engineer and no prints and, me not being an engineer and just a lowly electrical contractor, I'm in a bit of a learning curve balancing materials costs versus anticipated future need.
The loads on the low volt panel are minuscule: the two 1/2 hp fans, the unknown welder and 12 convenience receps @ 1,800VA/strap.
Anyone want to suggest a cost-efficient, expedient means of navigating this without cutting corners? What would happen if I just went with a Delta-Delta configuration off the Wye primary? Is there a way to avoid a stinger on a 3-p 240V service I am not aware of?
I visited the site to finalize some measurements for the lateral primary run and, while there, I noticed that the exhaust fans were in and I took a peek. They are 1/2hp 240V with an FLA of 3.3 or 6.6 if connected to 120V. While there, I was also informed that I needed to add a "typical" (his words) receptacle for a welder - standard 240V., 50A supply.
This throws all of my calcs. If those fans were 230V. listed I might, and I do mean might, take a chance on a 208V supply. But with a plate rating of 240V I am not comfortable chancing it.
All of this swimming around in my head for the last couple of days has done nothing but confuse me. I know the answer is drop dead simple, but it isn't coming to me.
So...
That the MDP is 480, 3-phase in a Wye configuration from the CTs, I have two options that I can see:
1. 208V 3-phase Wye secondary off a 45KVA xfmr and hook up the exhaust fans to single phase 120 and make him buy a welder to accommodate my service;
2. A Wye/Delta 240V 3-phase xfmr, also 45KVA, center tapped for some 2-pole 240 and a 208V stinger that will never be used anywhere for anything and will unbalance the secondary panel.
One of the overriding issues I have, and I'm hoping for some input on this, is that the bids are in. Obviously I will have to recalculate everything and resubmit my price, but I want to make sure his expansion needs are covered to the best of my ability without soaking the material budget with needless excess. This job has no engineer and no prints and, me not being an engineer and just a lowly electrical contractor, I'm in a bit of a learning curve balancing materials costs versus anticipated future need.
The loads on the low volt panel are minuscule: the two 1/2 hp fans, the unknown welder and 12 convenience receps @ 1,800VA/strap.
Anyone want to suggest a cost-efficient, expedient means of navigating this without cutting corners? What would happen if I just went with a Delta-Delta configuration off the Wye primary? Is there a way to avoid a stinger on a 3-p 240V service I am not aware of?