We are working on a project that involves remote electronic metering of various panelboards & switchboards, etc.
The components (meter, CT's, PT's, fuse block, shorting terminal block, etc.) are all UL listed & approved by the AHJ, including the NEMA 3R 18" x 24" hinge cover enclosure the components are to be installed in.
The components are being installed per the client's standard, pertaining to wire size, mounting methods, clearances, etc. & being done so per code. Is there anything in the code, or a UL requirement that these components assembled in the field need to be NRTL (nationally recognized testing lab) as an "assembly" & have a separate NRTL label attached?
Where is the cut-off point when NRTL labeling is concerned?
Example 1: take a 4 sq. j-box & connect a 1/2" conduit, install 2#12 wires with a wire nut, is this now considered an "assembly" & requires a NRTL label, even though each component is NRTL & installed per their manufacturer's requirements?
Example 2: install a Watt Stopper power pack in the same j-box... you just changed the previous "assembly"... does that mean that a new NRTL label is now required?
Example 3: take a NEMA 3R 12" x 12" pull can & install a lighting contactor & wires, etc., a common installation done all across the country... is this considered an "assembly" & therefore would require a separate NRTL label?
I know that NEC Article 110.2 & definitions for "Approved", "Labeled" & "Listed" clearly state that the AHJ has the say over what does & does not require a NRTL label, but the AHJ in this case does not clearly identify that an "assembly" of listed components is required to have a separate NRTL label... neither does NEC, nor OSHA.
Obviously, it would open a huge can of worms if every "assembly" of NRTL components would require separate testing/listing, when there are literally millions of installations across the nation where this would be required.
If someone could shed light on this, I'd appreciate it.
Thanks!
Thanks!