Hello,
For an 240 volt 600 amp Service (480 amp load) we've got almost an 90m span of triplex that the Pole Contractor suggests will be no problem for an double run of NS90 4/0 Triplex...(although I asked for 266kcmil it is apparently very difficult to get.)
Table 36A for maximum allowable ampacity for aluminum neutral supported cable has no derating references.... is there an formula for derating open wiring ?
Thanks for any feedback!
For an 240 volt 600 amp Service (480 amp load) we've got almost an 90m span of triplex that the Pole Contractor suggests will be no problem for an double run of NS90 4/0 Triplex...(although I asked for 266kcmil it is apparently very difficult to get.)
Table 36A for maximum allowable ampacity for aluminum neutral supported cable has no derating references.... is there an formula for derating open wiring ?