Sric
Member
- Location
- Prescott,Wi,usa
i have a 350kw gen set. I will be fusing the generator brkr at 500a. I've been working with the local inspector and nothing seems black and white so I'm looking for code ref. to go along with all advice. the gen set is feeding a 3 pole ats. the ats will be feeding a distribution panel with 3 phase loads only. lieberts, pumps, dry coolers, etc.... it will also feed a ups which will feed a 480/120/208 transformer where we will be deriving out neutral for some 120v loads. The intent is not to run the neutral from the main service feed or from the gen set to the ats. this has been debated between me and the inspector weather or not i have to run the neutral. i dont believe i do but what then is the correct way to handle the xo termination at the gen set. i believe i can bond it because i'm not creating a parallel path for the neutral current because there is no neutral. also it has been debated if i can run parallel 4/0 to feed the distribution panel. 4/0 are good for 230a run parallel equals 460a. next size brkr is 500a. any thoughts and code ref. would be greatly appreciated.