nuetral in swich boxes

Status
Not open for further replies.

liquidtite

Senior Member
Location
Ny
im aware of the recent code change witch states that you must bring a nuetral to the switch boxes.I always thought this code applied to residential only, and I dont have 08 0r 11 nec on hand,but this rule came up in specs that im working on in a hospital. I was just woundering what is the pupose behind this code change?
 
Last edited:
The rule 404.2(C) applies to light switch locations in all occupancies. The reason for the rule is the fact that the manufacturer's of electronic switching devices were using the EGC as a grounded conductor to power the electronics in their devices. This is (was) permitted by the product standard as long as the current on the EGC was 1/2mA or less per device. This current on the EGC is a shock hazard for someone working on the EGC. UL said that the standard would not be changed unless the NEC required the grounded conductor to be present at the light switch location.
 
There are exceptions that basically cover conditions where the neutral could easily be added later such as a conduit with sufficient area to add the wire. That's why some folks think it does not apply to non-residential locations.
 