Re: Nuetrals in a panel
FWIW-
Had my holiday interrupted last Thanksgiving when an improperly installed "two-gang" panel. What had happened was that there had been no neutral wire run; the neutral bar in the second panel had been bonded to the case, and any imbalance drained through the case to the ground bus in the neighboring panel. Worked fine, untill 30 years' worth of vibration, rust, etc. opened the path.
After running maybe 6 ft. of feeder-size wire to the neutral bus, and removing the bonding screw, and connecting the ground busses with #8, all is well; the IT guys immediately reported the clearing up of several gremlins in their network.
Lesson: There is only one main panel. Everything else, even if it's just as big, and right next to it, should be treated as a sub-panel.