I have a 480 volt single phase 2kva transformer with protection only on the primary side with a 8 amp D curve breaker. I sized the breaker using NEC 450.3B. 2000/480 = 4.2 amps. Since it is less than 9 amps I use 167% of 4.2 which equals 7.014 amps reason for 8 amp breaker. I get these nuisance trips. Not sure if the trips are associated with inrush current from the transformer or a load turning on during the cycle of the equipment? Not sure what to look for. I was told to up the breaker to 10 amps. If I do this, I would think I would need to protect the secondary side. The trips are not always on start up.