..measurements of the line to neutral voltages vs. loading applied on one phase could be used to determine if there is a bad neutral.
Thanks for explaining this.
Never understood how line voltage occurs from Neutral to Grounding, much less how something in between occurs after shutting off the breaker.
Like a good knucklehead, if solenoid tester wont remove confusion we re-terminate replacements per 460.4(D) & 110.14.
Don't need to think about why crap won't work if we just remove it, like panel flippers, and builders that insist on re-wring the entire building.
But now I see, impedance from carbonized or broken Neutrals change N-G potential from near Zero to line voltage.
And for ~line voltages after shut down, my knuckle head can now visualize the cross-tied circuit.